For a 100-kVA, 3-phase transformer, what is the maximum size of the primary overcurrent device?

Get ready for your Rigging and Hoisting Exam with our comprehensive study material. Leverage multiple choice questions, answers, and insights to gain confidence and succeed in your rigging career!

To determine the maximum size of the primary overcurrent device for a 100-kVA, 3-phase transformer, we begin with the formula to calculate the full-load primary current. This is essential because the primary overcurrent device is usually rated based on the transformer's full-load primary current.

The full-load current for a 3-phase transformer is given by the formula:

[ I_{primary} = \frac{KVA \times 1000}{\sqrt{3} \times V_{primary}} ]

Where:

  • KVA is the rating of the transformer (100 kVA in this case).

  • ( V_{primary} ) is the line-to-line voltage of the primary side.

Assuming a commonly used primary voltage of 480V, the calculation would look like this:

[ I_{primary} = \frac{100 \times 1000}{\sqrt{3} \times 480} \approx 120.2 A ]

For protection devices, the National Electrical Code (NEC) allows an overcurrent protection device to be sized at 125% of the full-load current for transformers. Thus, we can calculate:

[ Maximum\ Overcurrent\ Protection = I_{primary} \times